    Quote Originally Posted by namvet View Post
    damned. not good.



    so you have the ungrounded sockets. it really needs to be upgraded bad. im surprised it wasn't some time in the past. to meet code.
    you said when lowered the fan the light came on. right?? if it didn't trip a breaker that's a bad connection. or what i call a malfuction at the junction. are the wires taped together?? I never use tape but instead wire nuts.




    their cheap, code approved and fast to install. a good tight connection. so. if these wires are taped remove it and replace with the nuts. you may very well find your problem under the tape.
    My bad, the other outlets do have the 3 prongs. I was replying incorrectly. The switches in this project were 3 way switches, one hot and 2 travellers wires. I "assumed" the others were 2 pin connectors, as in black/white, as opposed to the travellers, but they are 3 pronged and grounded.

    The connections in the ceiling were in fact made with the wire connectors, but I also put a ton of electrical tape around them as well, in addition to the wiring up to where it met the ceiling.

  2. Thanks Gunny thanked this post
  3. #62
    Join Date
    May 2008
    Location
    Missouri
    Posts
    8,256
    Thanks (Given)
    951
    Thanks (Received)
    3923
    Likes (Given)
    0
    Likes (Received)
    0
    Piss Off (Given)
    0
    Piss Off (Received)
    0
    Mentioned
    22 Post(s)
    Rep Power
    4457675

    Default

    Quote Originally Posted by jimnyc View Post
    My bad, the other outlets do have the 3 prongs. I was replying incorrectly. The switches in this project were 3 way switches, one hot and 2 travellers wires. I "assumed" the others were 2 pin connectors, as in black/white, as opposed to the travellers, but they are 3 pronged and grounded.

    The connections in the ceiling were in fact made with the wire connectors, but I also put a ton of electrical tape around them as well, in addition to the wiring up to where it met the ceiling.
    Jesus saves. so your up to code. are the wire connectors actually wire nuts?? you may need to just tighten them up. but there is a bad connection up there somewhere. a good eyeball inspection goes a long way here

  4. Thanks Gunny thanked this post
  5. #63
    Join Date
    Jan 2007
    Location
    The Republic of Texas
    Posts
    48,237
    Thanks (Given)
    34626
    Thanks (Received)
    26699
    Likes (Given)
    2540
    Likes (Received)
    10174
    Piss Off (Given)
    0
    Piss Off (Received)
    12
    Mentioned
    374 Post(s)
    Rep Power
    21475530

    Default

    Quote Originally Posted by namvet View Post
    Jesus saves. so your up to code. are the wire connectors actually wire nuts?? you may need to just tighten them up. but there is a bad connection up there somewhere. a good eyeball inspection goes a long way here
    Yes, he's talking about wire nuts. Took me a minute to figure that one out back on page one.

    My grandfather was an electrician and he called them "caps". Terminology is a BIG problem in the electrical trade. It varies from company to company, and person to person. Deciphering WTH the guy your listening to is talking about is half the battle.
    “When bad men combine, the good must associate; else they will fall, one by one, an unpitied sacrifice in a contemptible struggle.” Edumnd Burke

  6. #64
    Join Date
    May 2008
    Location
    Missouri
    Posts
    8,256
    Thanks (Given)
    951
    Thanks (Received)
    3923
    Likes (Given)
    0
    Likes (Received)
    0
    Piss Off (Given)
    0
    Piss Off (Received)
    0
    Mentioned
    22 Post(s)
    Rep Power
    4457675

    Default

    Quote Originally Posted by Gunny View Post
    Yes, he's talking about wire nuts. Took me a minute to figure that one out back on page one.

    My grandfather was an electrician and he called them "caps". Terminology is a BIG problem in the electrical trade. It varies from company to company, and person to person. Deciphering WTH the guy your listening to is talking about is half the battle.
    well if his wiring is up to code that's the important thing. im with you. he should just hire a pro electrician to fix this and problem solved. trying to fix tech problems on the net can be a pain.

  7. #65
    Join Date
    Jan 2007
    Location
    The Republic of Texas
    Posts
    48,237
    Thanks (Given)
    34626
    Thanks (Received)
    26699
    Likes (Given)
    2540
    Likes (Received)
    10174
    Piss Off (Given)
    0
    Piss Off (Received)
    12
    Mentioned
    374 Post(s)
    Rep Power
    21475530

    Default

    Quote Originally Posted by namvet View Post
    well if his wiring is up to code that's the important thing. im with you. he should just hire a pro electrician to fix this and problem solved. trying to fix tech problems on the net can be a pain.
    Sounds like he got it right. He just had his travellers crossed. As far as getting up to code is concerned, you're only up to code for a max of 4-5 years. That's how often they update that $100. NEC code book. A lot of code is overkill and purposefully so. That 1940's house would probably cost him $5K to bring up to code.

    As I stated previously, most electrical problems are either the user's appliances, or the devices. Not the wiring. The BIGGEST problem I've seen is the know it all, wannabe's overloading their panels and/or circuitry.
    “When bad men combine, the good must associate; else they will fall, one by one, an unpitied sacrifice in a contemptible struggle.” Edumnd Burke

  8. Thanks fj1200 thanked this post
  9. #66
    Join Date
    May 2008
    Location
    Missouri
    Posts
    8,256
    Thanks (Given)
    951
    Thanks (Received)
    3923
    Likes (Given)
    0
    Likes (Received)
    0
    Piss Off (Given)
    0
    Piss Off (Received)
    0
    Mentioned
    22 Post(s)
    Rep Power
    4457675

    Default

    Quote Originally Posted by Gunny View Post
    Sounds like he got it right. He just had his travellers crossed. As far as getting up to code is concerned, you're only up to code for a max of 4-5 years. That's how often they update that $100. NEC code book. A lot of code is overkill and purposefully so. That 1940's house would probably cost him $5K to bring up to code.

    As I stated previously, most electrical problems are either the user's appliances, or the devices. Not the wiring. The BIGGEST problem I've seen is the know it all, wannabe's overloading their panels and/or circuitry.
    ive owned 2 homes and never had one update required

  10. Thanks Gunny thanked this post
  11. #67
    Join Date
    Aug 2008
    Location
    In your head
    Posts
    24,075
    Thanks (Given)
    4300
    Thanks (Received)
    4683
    Likes (Given)
    1449
    Likes (Received)
    1140
    Piss Off (Given)
    0
    Piss Off (Received)
    39
    Mentioned
    47 Post(s)
    Rep Power
    9173683

    Default

    Quote Originally Posted by Gunny View Post
    As I stated previously, most electrical problems are either the user's appliances, or the devices. Not the wiring. The BIGGEST problem I've seen is the know it all, wannabe's overloading their panels and/or circuitry.
    A friend bought a new house in the neighborhood and I went into one small bedroom, about 10 by 10, and it had no less than 20 outlets packed into that one room. I don't even know what that could be used for but thankfully when they update it'll be ripped out when an actual electrician goes in there.
    "when socialism fails, blame capitalism and demand more socialism." - A friend
    "You know the difference between libs and right-wingers? Libs STFU when evidence refutes their false beliefs." - Another friend
    “Don't waste your time with explanations: people only hear what they want to hear.” - Paulo Coelho


  12. Thanks Gunny thanked this post
  13. #68
    Join Date
    Jan 2007
    Location
    The Republic of Texas
    Posts
    48,237
    Thanks (Given)
    34626
    Thanks (Received)
    26699
    Likes (Given)
    2540
    Likes (Received)
    10174
    Piss Off (Given)
    0
    Piss Off (Received)
    12
    Mentioned
    374 Post(s)
    Rep Power
    21475530

    Default

    Quote Originally Posted by fj1200 View Post
    A friend bought a new house in the neighborhood and I went into one small bedroom, about 10 by 10, and it had no less than 20 outlets packed into that one room. I don't even know what that could be used for but thankfully when they update it'll be ripped out when an actual electrician goes in there.
    Uh, yeah. You can put 13.3 receptacles on one 20 amp circuit, if they are general purpose outlets (don't carry a continuous load). The math to a 20 amp circuit is 80% of the max load. That's roughly 16 amps per circuit. The panel is configured the same way. 80% of maximum load. Almost all houses have 200 amp panels. That's roughly 160 amps max load. Most houses are wired bare minimum. The developers and contractors want to keep cost to a minimum.

    The size of the room doesn't matter. What matters is the above. That room would have to have 2 circuits, minimum, on its own. I somehow doubt that's the case unless that was custom built that way.
    “When bad men combine, the good must associate; else they will fall, one by one, an unpitied sacrifice in a contemptible struggle.” Edumnd Burke

  14. Thanks fj1200 thanked this post
  15. #69
    Join Date
    Aug 2008
    Location
    In your head
    Posts
    24,075
    Thanks (Given)
    4300
    Thanks (Received)
    4683
    Likes (Given)
    1449
    Likes (Received)
    1140
    Piss Off (Given)
    0
    Piss Off (Received)
    39
    Mentioned
    47 Post(s)
    Rep Power
    9173683

    Default

    ^I'm sure you would have just walked out shaking your head. It was mind boggling.
    "when socialism fails, blame capitalism and demand more socialism." - A friend
    "You know the difference between libs and right-wingers? Libs STFU when evidence refutes their false beliefs." - Another friend
    “Don't waste your time with explanations: people only hear what they want to hear.” - Paulo Coelho


  16. Thanks Gunny thanked this post
  17. #70
    Join Date
    Sep 2014
    Posts
    202
    Thanks (Given)
    89
    Thanks (Received)
    183
    Likes (Given)
    0
    Likes (Received)
    0
    Piss Off (Given)
    0
    Piss Off (Received)
    0
    Mentioned
    0 Post(s)
    Rep Power
    112654

    Default

    Those wiring schematics suck especially if you have multiple on/off switches and fan/light combos also.

    Fuck that.

    I'll climb down into the septic tank in rubber boots to clean it out with a shovel before I try rewiring something like that.
    Hold my beer for a sec...

  18. Thanks Gunny thanked this post
  19. #71
    Join Date
    Jan 2007
    Location
    The Republic of Texas
    Posts
    48,237
    Thanks (Given)
    34626
    Thanks (Received)
    26699
    Likes (Given)
    2540
    Likes (Received)
    10174
    Piss Off (Given)
    0
    Piss Off (Received)
    12
    Mentioned
    374 Post(s)
    Rep Power
    21475530

    Default

    Quote Originally Posted by fj1200 View Post
    ^I'm sure you would have just walked out shaking your head. It was mind boggling.
    Depends on whether or not I was getting paid.

    $25. an hour can buy you a LOT of electrical expertise. But that includes the 3-4 hours it takes for me and a calculator to figure the load on your panel and circuitry before I even start rewiring.
    “When bad men combine, the good must associate; else they will fall, one by one, an unpitied sacrifice in a contemptible struggle.” Edumnd Burke

  20. #72
    Join Date
    Jan 2007
    Location
    The Republic of Texas
    Posts
    48,237
    Thanks (Given)
    34626
    Thanks (Received)
    26699
    Likes (Given)
    2540
    Likes (Received)
    10174
    Piss Off (Given)
    0
    Piss Off (Received)
    12
    Mentioned
    374 Post(s)
    Rep Power
    21475530

    Default

    Quote Originally Posted by Baba Booey View Post
    Those wiring schematics suck especially if you have multiple on/off switches and fan/light combos also.

    Fuck that.

    I'll climb down into the septic tank in rubber boots to clean it out with a shovel before I try rewiring something like that.
    Reading schematics is easy. But I do it all the time. First time I looked at a schematic, I turned it upside down trying to figure it out.
    “When bad men combine, the good must associate; else they will fall, one by one, an unpitied sacrifice in a contemptible struggle.” Edumnd Burke

  21. Thanks Baba Booey thanked this post
  22. #73
    Join Date
    Sep 2014
    Posts
    202
    Thanks (Given)
    89
    Thanks (Received)
    183
    Likes (Given)
    0
    Likes (Received)
    0
    Piss Off (Given)
    0
    Piss Off (Received)
    0
    Mentioned
    0 Post(s)
    Rep Power
    112654

    Default

    Quote Originally Posted by Gunny View Post
    Reading schematics is easy. But I do it all the time. First time I looked at a schematic, I turned it upside down trying to figure it out.
    I can't do that, I have a certain dyslexia. Seriously, I get my right/left fucked up all the time. East/West - I'm hopeless. My wife points instead of saying left or right anymore.

    Plus you already figured out, I'm comfortable around shit, so the septic tank is more user friendly for me.
    Hold my beer for a sec...

  23. Thanks Gunny thanked this post
  24. #74
    Join Date
    Jan 2007
    Location
    The Republic of Texas
    Posts
    48,237
    Thanks (Given)
    34626
    Thanks (Received)
    26699
    Likes (Given)
    2540
    Likes (Received)
    10174
    Piss Off (Given)
    0
    Piss Off (Received)
    12
    Mentioned
    374 Post(s)
    Rep Power
    21475530

    Default

    Quote Originally Posted by Baba Booey View Post
    I can't do that, I have a certain dyslexia. Seriously, I get my right/left fucked up all the time. East/West - I'm hopeless. My wife points instead of saying left or right anymore.

    Plus you already figured out, I'm comfortable around shit, so the septic tank is more user friendly for me.
    “When bad men combine, the good must associate; else they will fall, one by one, an unpitied sacrifice in a contemptible struggle.” Edumnd Burke

  25. #75
    Join Date
    May 2008
    Location
    Missouri
    Posts
    8,256
    Thanks (Given)
    951
    Thanks (Received)
    3923
    Likes (Given)
    0
    Likes (Received)
    0
    Piss Off (Given)
    0
    Piss Off (Received)
    0
    Mentioned
    22 Post(s)
    Rep Power
    4457675

    Default

    Quote Originally Posted by Gunny View Post
    Reading schematics is easy. But I do it all the time. First time I looked at a schematic, I turned it upside down trying to figure it out.
    maybe for you



    this shit gave me a headache. every day

  26. Thanks Baba Booey, Gunny thanked this post